Search found 14 matches

by Rakdos
22 May 2020, 15:06
Forum: Raccordement du Thermostat à la chaudière
Topic: Branchement sur WPMWII de Stiebel Eltron
Replies: 4
Views: 44

Re: Branchement sur WPMWII de Stiebel Eltron

Fin mot de l'histoire: pas compatible. En fait, le module WPMII lit le voltage en sortie pour savoir si un composant est dessus et s'il est actif ou non. Si le WPMII demande au composant de démarrer mais qu'il ne tire pas de jus dessus, c'est qu'il y a un problème (technique, coupure, etc) et donc l...
by Rakdos
22 May 2020, 15:00
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

If I plug the grey wire (from the relais) into this slot it may create a short circuit in the regulator and break it (eg the regulator is sending no voltage but Netatmo is sending high voltage). As I said before, the Netatmo Relais‘ grey wire doesn‘t send out anything else than what you „feed it“ o...
by Rakdos
19 May 2020, 14:54
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

And here is the result, it works as expected but it may create a huge issue in the regulator. The main reason is because the regulator drives the pumps state (ON-OFF) according to several temperature sensors (I've seen 10 of them per circuit). If I plug the grey wire (from the relais) into this slot...
by Rakdos
18 May 2020, 21:58
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

Thank you for your fast reply. I finished setting up the setup. I've ran some test yet and even if I say to NetAtmo "Heat the room up" the regulator does not activate the pump for the heating circuit but it receives the information to run (otherwise it's in "away" mode thanks to the wiring setup). I...
by Rakdos
18 May 2020, 17:42
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

Hi again ! I’m installing it up but I’m facing an issue. The suggested setup says to put the black wire to “2” but it’a the power network. Only the grey is linked to “3” but the black should be set on “4”, shouldn’t it ? And to make it work, I have to remove the bridge between “3” and “4”. That way,...
by Rakdos
17 May 2020, 23:38
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

Yes, exactly. It's what I've thought to do. I'm thinking to set the temperature in the heating circuit (the "system temperature") at - let's say - 30°C 24h/7d. Then the thermostat will drive the pump to reach the "room temperature" accordingly but I won't be able to reach 30° and above. If the room ...
by Rakdos
17 May 2020, 23:17
Forum: Attaching the Thermostat to the boiler
Topic: Attaching on WPMWII (Stiebel Eltron) - EDIT: incompatible
Replies: 17
Views: 105

Re: Attaching on WPMWII (Stiebel Eltron)

Actually I don't have a boiler, it's a heat pump (WPL 16S from Stiebel Eletron). The given attachment are linked to the Heat pump regulator (WPMW II from Stiebel Eletron). My setup also have a buffer water tank for the heating circuit. That said, I'll have to be patient in order to see if the heatin...
by Rakdos
17 May 2020, 23:06
Forum: Raccordement du Thermostat à la chaudière
Topic: Branchement sur WPMWII de Stiebel Eltron
Replies: 4
Views: 44

Re: Branchement sur WPMWII de Stiebel Eltron

S'en vient d'une discussion de confirmation de branchement que je ne traduirai pas ici. Je traduit tout même les opérations à réaliser: Couper l'arrivée électrique (tout de même...) Retirer le pont entre 2 et 3 (Fils du relais) Bleu sur 1 (Fils du relais) Marron sur 2 (Fils du relais) Noir sur 2 (Fi...
by Rakdos
17 May 2020, 23:04
Forum: Raccordement du Thermostat à la chaudière
Topic: Branchement sur WPMWII de Stiebel Eltron
Replies: 4
Views: 44

Re: Branchement sur WPMWII de Stiebel Eltron

N'étant pas sur des ponts indiqués, j'ai repris une photo et GEORGzer a effectivement raison. VO: Thank you for your very fast reply. It's really appreciated. The photo isn‘t perfect, am I right that there are two bridge wires, one going from „2“ to „3“ and one from „3“ to „4“? Yes you are absolutel...
by Rakdos
17 May 2020, 22:57
Forum: Raccordement du Thermostat à la chaudière
Topic: Branchement sur WPMWII de Stiebel Eltron
Replies: 4
Views: 44

Re: Branchement sur WPMWII de Stiebel Eltron

Solution offerte par GEORGzer sur la partie du forum en Anglais: https://forum.netatmo.com/viewtopic.php?f=19&t=18194&p=77072#p77068 VO: First of, the „3“ and „4“ labels are not standard on every setup. The photo isn‘t perfect, am I right that there are two bridge wires, one going from „2“ to „3“ an...