Baxi boiler and Netatmo thermostat

You need some help attaching the thermostat to your specific boiler. This way please !
sargro
Posts: 2
Joined: 17 Mar 2018, 13:55

Baxi boiler and Netatmo thermostat

Post by sargro »

Hello,

I have a Baxi Duo-Tec Compact+ 20 GA condesing combi boiler, and I am planning to buy the Netatmo thermostat. I currently do not have any thermostat
I have attached a couple of photos, of the boiler manual and how the wiring looks like right now.

My questions:

1. I have hydronic underfloor heating on two floors, with one boiler. The system is high inertia. Will the thermostat work with my system and account for the high inertia?
2. As I understand, I would connect the thermostat wires to the terminals 1 and 2 on the boiler, where the loop right now is (will remove that), and the L and N wires should be connected to the L and N terminals in the boiler, together with the wires currently there, correct?
3. I currently do not have WiFi, as the house is under construction. Will it still work as a "dumb" thermostat for the time being, or will it require initial set up through WiFi?
4. The boiler uses 230v in the terminal block where the thermostat should be connected. The relay is capable of the 230v switching, correct?

Thank you
Attachments
Capture3.JPG
Capture2.JPG
Capture1.JPG
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Baxi boiler and Netatmo thermostat

Post by GEORGzer »

I can‘t say anything specific to question 1, but I can‘t think of any reason why not. Your system will be controlled by the Netatmo Thermostat‘s schedule and will react to the room temperature wherever you place the thermostat.

2: correct. The Netatmo Relaise will have 4 wires: Brown/Blue will go to the L/N and Black/Grey will go to the terminals 1/2, replacing the existing bridge.

3: might be a problem because you‘ll need wifi to set the system up.

4: not a problem. The Netatmo Thermostat can be used for low and high voltage systems, since only a circuit between two contacts gets closed when it switches on.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
sargro
Posts: 2
Joined: 17 Mar 2018, 13:55

Re: Baxi boiler and Netatmo thermostat

Post by sargro »

Great, thank you for your reply.
I guess for the Wifi Issue, using my phone as a hotspot for the installation, and then just leaving it without wifi, could be a solution, right?
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Baxi boiler and Netatmo thermostat

Post by GEORGzer »

Could be. You won't be able to use the app after that, obviously. And I can't say if schedules will work when the system has no internet connection.
But since this will be temporary, you could give it a shot.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
marek27
Posts: 5
Joined: 09 Oct 2020, 19:06

Re: Baxi boiler and Netatmo thermostat

Post by marek27 »

Hi all,

I have the same Baxi boiler and have problem that the thermostat (relay) does not communicate with boiler.
In the atteched picture you can see original connection (without thermostat) / current connection (with thermostat).

Please can you help me where could I do a mistake or give me any tips?

Thank you
Attachments
121180119_642077050003542_6068342922174740985_n.jpg
121180119_642077050003542_6068342922174740985_n.jpg (64.16 KiB) Viewed 1008 times
121017222_3191968627580352_1000635603273572985_n.jpg
121017222_3191968627580352_1000635603273572985_n.jpg (43.86 KiB) Viewed 1008 times
121145436_745750142948332_1561854171998444204_n.jpg
121145436_745750142948332_1561854171998444204_n.jpg (112.94 KiB) Viewed 1008 times
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Baxi boiler and Netatmo thermostat

Post by GEORGzer »

Wiring seems to be correct. Does the Relais‘ LED light up?
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
marek27
Posts: 5
Joined: 09 Oct 2020, 19:06

Re: Baxi boiler and Netatmo thermostat

Post by marek27 »

Yes, the relais LED light up
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Baxi boiler and Netatmo thermostat

Post by GEORGzer »

Ok, could you please give us more informations.
Where there any issues during the setup process in the app?
Doesn’t your boiler react at all when you press the button on the Relais?
If not, can you make a test by putting the bridge wire back in place to rule out the boiler itself?
Thanks.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
marek27
Posts: 5
Joined: 09 Oct 2020, 19:06

Re: Baxi boiler and Netatmo thermostat

Post by marek27 »

There was not any problem with app setup.
I connected the relay to the boiler, then plugged power cable to power supply and if I start manually the relay it doesn't start the boiler. Also if I increase a temperature on the thermostat it does not start the heating on the boiler (see picture).
The boiler doesn't react at all when I press the button on the Relais.

Can you please more specify the last point? Should I disconnect all cables of thermostat and put the bridge back ? What I can find out if I do this?

Thank you for your time
Attachments
121234869_3422168824487770_7297419602583056304_n.jpg
121234869_3422168824487770_7297419602583056304_n.jpg (45.88 KiB) Viewed 1004 times
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Baxi boiler and Netatmo thermostat

Post by GEORGzer »

I want to rule out wrong settings on the boiler.
Switch off the power, disconnect the Relais grey and black wires and replace them with the bridge wire that was installed.
Then switch the power back on.
If your boiler starts then the issue lies with the Relais.
If it doesn‘t start then we have to take a look at the boiler‘s settings.

Does the Relais make a clicking sound when you increase the temperature over the set-point?
Note: The Thermostat does too, so perhaps move it away before listening.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
Post Reply