Hello,
can someone help me to identify where to plug the wires on the boiler? My boiler is a riello start 25 and i want to wire the Relais directly to the boiler and use the Thermostat wirelessly (wireless setup). I have a photo of the board.
Connecting Smart thermostat to a Riello Start 25 boiler
Connecting Smart thermostat to a Riello Start 25 boiler
- Attachments
-
- IMG_0154-min.JPG (1.12 MiB) Viewed 630 times
Re: Connecting Smart thermostat to a Riello Start 25 boiler
You have to replace the jumper on the grey terminals with the black and grey wires of the Netatmo Relais, polarity not important.
Then you have to add the blue and bronw wires to the boiler‘s power supply
You can find in the manual instructions on the boiler‘s settings.
https://www.riello.com/international/pr ... PL-0006097
Then you have to add the blue and bronw wires to the boiler‘s power supply
You can find in the manual instructions on the boiler‘s settings.
https://www.riello.com/international/pr ... PL-0006097
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors
Not a Netatmo employee
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors
Not a Netatmo employee
Re: Connecting Smart thermostat to a Riello Start 25 boiler
Thanks for the response. The grey and black wires i think that it's simple, but the power blue and brown wires how do i connect? On the same place of the existing blue and brown wires?
Re: Connecting Smart thermostat to a Riello Start 25 boiler
Yes. You switch off the power, then you unscrew the blue and brown wires form the terminal (photo) on one side. Preferably the boiler‘s side (bottom of the photo) and not the one the supply wires are attached to, but if it‘s easier that way then it‘s ok as well.
Then you add the Relais wires, matching the colors and you tighten the screws as much as you can.
Then you add the Relais wires, matching the colors and you tighten the screws as much as you can.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors
Not a Netatmo employee
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors
Not a Netatmo employee
Re: Connecting Smart thermostat to a Riello Start 25 boiler
Ok i understood. Thank you so much for your help