I am right now testing the thermostat and it seems that the boiler is continuously working.
I think it is due to the low range of temperature and because the thermostat manteins the temperature constant to 21ºC. Is it possible to configure the thermostate for instance 21ºC and when the temperature goes down to 20ºC, the boiler starts? until the temperature is 21,5ºC for example. I do not find this possibility in the configuration.

Brieuc_Netatmo
Posts: 2966
Joined: 02 Jan 2014, 11:20

Re: Boiler working constantly

Post by Brieuc_Netatmo » 02 Dec 2014, 10:22

Hello,
I've check the behaviour of your Thermostat and everything seems to work perfectly.
If you want to increase the heating demand threshold, you can set higher value for hysteresis in the advanced settings of the application.