Re: Advanced algorithms (PID and Heating Prediction) computa

Posted: 17 Nov 2018, 11:12
by pawelf1
Will PID will work corectly when i have a boiler with external thermometer that depending on outside tempreture setups temp of heating water in my home?

Ex: 10 degress outside radiators are at 35 degress
-10 degress outside radiator are at 55 degress

Re: Advanced algorithms (PID and Heating Prediction) computa

Posted: 17 Nov 2018, 19:39
by pebbleridge13
pawelf1 wrote:Will PID will work corectly when i have a boiler with external thermometer that depending on outside tempreture setups temp of heating water in my home?

Ex: 10 degress outside radiators are at 35 degress
-10 degress outside radiator are at 55 degress
Hi,

Your Boiler Outside Compensation Control will totally confuse the Netatmo PID and Heating Prediction calculations.

From my experience I suggest you disable your Outside Compensation as my Netatmo does a fantastic job of controlling the temperature and heating start times on it's own.

Regards,

Paul

Re: Advanced algorithms (PID and Heating Prediction) computa

Posted: 18 Nov 2018, 10:06
by stanikuz
pawelf1 wrote:Will PID will work corectly when i have a boiler with external thermometer that depending on outside tempreture setups temp of heating water in my home?

Ex: 10 degress outside radiators are at 35 degress
-10 degress outside radiator are at 55 degress
As pebbleridge13 already said: you should turn off this boiler's feature. Or you can turn off Auto-Adapt function of Netatmo Energy ecosystem. Just look at last paragraph of this page:
https://www.netatmo.com/en-us/helpcente ... -i-do/69_A

Re: Advanced algorithms (PID and Heating Prediction) computation

Posted: 27 Nov 2019, 09:46
by lottware
Is this algorithm compatible/recommended can it be fine if a pellet stove is also used to heat?

Re: Advanced algorithms (PID and Heating Prediction) computation

Posted: 29 Nov 2019, 09:05
by sergeantd
lottware wrote:
27 Nov 2019, 09:46
Is this algorithm compatible/recommended can it be fine if a pellet stove is also used to heat?
Last year I used to have a pellet stove as heating system with PID enabled. So I can tell that it was working properly, but for better results you have to use the “always on” function of your pellet stove so you will always have hot water waiting for your demand.