thermostat in room without valve

Post Reply
lottware
Posts: 3
Joined: 11 Oct 2019, 22:12

thermostat in room without valve

Post by lottware » 05 Nov 2019, 15:01

Hello,
I have a thermostat (connected to the boiler cables) and 7 thermostatic valves installed in the 7 radiators of the house.
The thermostat is in a room (and in a virtual room) without radiators and valves.
What happens if the thermostat detects a lower temperature in his room and at the same time all other valves detect a temperature that does not require heating to be switched on?

Example:
Thermostat room: 18° / 19 scheduled
Valve Room 1: 20° / 19 scheduled
Valve Room 2: 19° / 19 scheduled

I hope I explained myself correctly

C.

AcidBurn
Posts: 25
Joined: 27 Nov 2017, 12:08

Re: thermostat in room without valve

Post by AcidBurn » 05 Nov 2019, 16:31

Hi Lottware,

If I understand well your setup, if the thermostat alone in the virtual room drop below the consigne like in your exemple, that will turn on the heating.
But as all your valves will be close, I think the circulator of your heater will have a little problem as the water can't circulate.

Tommaso Florino
Posts: 61
Joined: 19 Jan 2018, 17:48

Re: thermostat in room without valve

Post by Tommaso Florino » 06 Nov 2019, 21:34

with your configuration I would highly recommend to set the system in Comfort mode, so your valves will be able to turn on/off heating; then put thermostat setpoint to a very low temperature

lottware
Posts: 3
Joined: 11 Oct 2019, 22:12

Re: thermostat in room without valve

Post by lottware » 25 Nov 2019, 17:35

AcidBurn wrote:
05 Nov 2019, 16:31
Hi Lottware,

If I understand well your setup, if the thermostat alone in the virtual room drop below the consigne like in your exemple, that will turn on the heating.
But as all your valves will be close, I think the circulator of your heater will have a little problem as the water can't circulate.
Exactly.
But the Netatmo system should know it is in this condition, isn't it?
In my case the thermostat commands the boiler on / off so I can't move it to another room.
Tommaso Florino wrote:
06 Nov 2019, 21:34
with your configuration I would highly recommend to set the system in Comfort mode, so your valves will be able to turn on/off heating; then put thermostat setpoint to a very low temperature
Yes, i am already in "Comfort Mode" - i can't understand if the system, knowing my configuration, turns on the thermostat always leaving at least one valve open. I don't know if I can explain myself
ITA: non so se riesco a spiegare la mia situazione ho TUTTI i termosifoni con valvole ma la stanza dov'è presente il termostato NON ha termosifoni (quindi non ha valvole).

Tommaso Florino
Posts: 61
Joined: 19 Jan 2018, 17:48

Re: thermostat in room without valve

Post by Tommaso Florino » 27 Nov 2019, 13:39

Ciao, non credo che il termostato su preoccupi di controllare se le valvole sono aperte o no. comunque nella tua configurazione non ti serve che il termostato faccia partire il riscaldamento, tanto hai termosifoni solo dove ci sono le valvole, quindi lascia che siano loro a decidere. cioè metti il setpoint del termostato ad una temperatura molto bassa, così lui non chiederà mai di riscaldare.

Tommaso Florino
Posts: 61
Joined: 19 Jan 2018, 17:48

Re: thermostat in room without valve

Post by Tommaso Florino » 27 Nov 2019, 13:42

inoltre : But the Netatmo system should know it is in this condition, isn't it? no! potrebbe anche essere che nella stanza del termostato ci sia un termosifone senza valvola.
In my case the thermostat commands the boiler on / off so I can't move it to another room. non è chiaro perché dici così. il relè da l'impulso alla caldaia( dietro comando del termostato o delle valvole) il termostato lo puoi spostare dove vuoi. è il relè che deve stare dove può essere cablato alla caldaia