Re: Valves not closing after a few days

Posted: 07 Dec 2017, 11:02
by Brieuc_Netatmo
whnagel wrote:6.12. System works as desired only in zon2 I see overheating peek with 4.7 degrees at 13:15 pm
In zone1 is one room who has a schedule with 23 degree between 12 an 2 pm. And hot water is circulating valve not closed I think
Perhaps netatmo can say something.
Hi,
Could you please let us know the serial number of the Valve(s) of this room?

Re: Valves not closing after a few days

Posted: 07 Dec 2017, 11:38
by whnagel
Zone2 valve serial 25:a5 and 25:af
Thanks for investigating

Re: Valves not closing after a few days

Posted: 07 Dec 2017, 11:45
by mdillmann
Brieuc,
for all valves but one the situation has improved dramatically. Thank you for that.

For my bathroom, the valve still does not close fully, I just touched the radiator and it is warm (not full-power but still heating) but no request for heat is needed and displayed in the app:
Screenshot-2017-12-7 Netatmo.png
The radiator has the connecting terminals (hot/cold) at the bottom, thus the valve sits only about 15cm above the floor.

Netatmo station in the same room also measures temperature still quite differently:
Screenshot-2017-12-7 quellenweg.png
Screenshot-2017-12-7 quellenweg.png (11.28 KiB) Viewed 336 times
I have customer-support case JUV-ZKYFX-016 open for this and granted access.

Let me know if you need anything more (eg. photo of the radiator) to track down the issue.


Thanks,
-Markus

Re: Valves not closing after a few days

Posted: 07 Dec 2017, 14:43
by whnagel
7.12. system works as desired.
About overheating in Zone2: today was not a usual day because we had craftsman here and the window was open from about 2 pm and we had an issue with our boiler in the morning therefore the boiler was completely off from 8 am til 11:30 am for maintenance.
Tomorrow I report again.

Re: Valves not closing after a few days

Posted: 08 Dec 2017, 09:26
by 2Qt2beStr8
Please push the update to my Relais

Re: Valves not closing after a few days

Posted: 09 Dec 2017, 03:48
by whnagel
8.12. system works as desired

Today overheat peek in zone2 was only 2,3 degree

Re: Valves not closing after a few days

Posted: 09 Dec 2017, 10:41
by NeilF
whnagel wrote:8.12. system works as desired

Today overheat peek in zone2 was only 2,3 degree
But isn't the main thing, if the valve was open or telling the heating to come on?

The room in question may well go over the desired temp (eg: because the thermostat is under temp), but if the valve in the room is telling the boiler to come on, or allowing the valve to open when the rooms temp has been met, that's a problem!?

Re: Valves not closing after a few days

Posted: 09 Dec 2017, 12:52
by whnagel
@neilf no heat request in zon2 and associated valves the whole day.
But heat requests from zone1 during the day. Conclusion the 2 valves in the thermostatroom in zone2 are not closing full. Overheating is the result. My zone2 is under investigation from Netatmo. I report each day my zone2 overheating to see if it’s getting better. I do no calibration just let the system work.

Re: Valves not closing after a few days

Posted: 09 Dec 2017, 23:18
by whnagel
9.12. System works as it should

No overheating in zone2 because zone1 had a constant plan with 18 degrees whole day

Re: Valves not closing after a few days

Posted: 12 Dec 2017, 10:31
by whnagel
10.12. no overheating same as 9.12.
11.12. overhearing zone2 max 3 degree