Post Reply
gosmart
Posts: 7
Joined: 31 Aug 2017, 15:34

Leaving the old thermostat in parallel?

Post by gosmart »

I am thinking about leaving the old thermostat in parallel as a backup to override Netatmo in case of some failure.

Normally, old would be set to 0 deg C, so it would not turn on the boiler.

Any reason why not to connect in such way?
rnucci
Posts: 35
Joined: 11 Jan 2016, 15:39

Re: Leaving the old thermostat in parallel?

Post by rnucci »

i use netatmo in parallel with the original boiler thermostat (needed for my boiler settings).
No problems at all
gosmart
Posts: 7
Joined: 31 Aug 2017, 15:34

Re: Leaving the old thermostat in parallel?

Post by gosmart »

Connected to the same terminals?
That's what I had in mind. Not just parallel use. Electrically connected in parallel.
rnucci
Posts: 35
Joined: 11 Jan 2016, 15:39

Re: Leaving the old thermostat in parallel?

Post by rnucci »

gosmart wrote:Connected to the same terminals?
That's what I had in mind. Not just parallel use. Electrically connected in parallel.
i don't see any potential problem... connecting wires to both thermostats you just make a logical OR: if one thermostat OR the other closes the circuit, the boiler starts
gosmart
Posts: 7
Joined: 31 Aug 2017, 15:34

Re: Leaving the old thermostat in parallel?

Post by gosmart »

My thoughts exactly.
It should work if netatmo is on-off thermostat. I don't know how to verify such assumption.
rnucci
Posts: 35
Joined: 11 Jan 2016, 15:39

Re: Leaving the old thermostat in parallel?

Post by rnucci »

gosmart wrote:My thoughts exactly.
It should work if netatmo is on-off thermostat. I don't know how to verify such assumption.
Netatmo IS an on-off thermostat. It just closes or opens a circuit
gosmart
Posts: 7
Joined: 31 Aug 2017, 15:34

Re: Leaving the old thermostat in parallel?

Post by gosmart »

Ok. Thanks!
R32er
Posts: 13
Joined: 09 Dec 2017, 18:13

Re: Leaving the old thermostat in parallel?

Post by R32er »

Hey guys. I am at the same question. Have an buderus gb112 and I need the old thermostat to set the water boiler.

My thought Is to connect the Netatmo Thermostat parallel too. the questionis if the Netatmo would override the old thermostat when the old is set to 0 degree.