Grant 50/90 Oil Boiler: connecting the wireless Thermostat

You need some help attaching the thermostat to your specific boiler. This way please !
Post Reply
Moose
Posts: 3
Joined: 06 Jul 2020, 23:21

Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by Moose »

Hi,

Great forum and I've been trawling it for an answer but can't find it, so I'm reaching out directly. I do apologies if this has been answered a bunch of times before but I couldn't find it.

I've a Grant 50/90 boiler with a basic analogue timer which just turns it on and off.

I had assumed I could leave this connected and turned to permanently "ON" and then connect the wireless RELAY to the boiler as a thermostat to override it. There wasn't a room thermostat ever fitted, as far as I can make out.

Here's the Grant wiring diagram:

Screenshot 2020-07-06 at 22.30.42.png
Screenshot 2020-07-06 at 22.30.42.png (43.01 KiB) Viewed 1006 times


Here's an image of what I had before I started:


Screenshot 2020-07-06 at 22.32.14.png
Screenshot 2020-07-06 at 22.32.14.png (527.45 KiB) Viewed 1006 times


So, I connected the RELAY as such:

Brown to Switched Live from Prgrammer (1)
Blue to to Mains Neutral (3)
Grey to (5) To CH valve if required
Black to (6) and removed the yellow looped wire

The RELAY gets power but it seems that the boiler just stays on constantly and the Thermostat has no effect on it.

I've triple checks all the wires are securely in place and can only assume I've placed the Black/Grey wires in the incorrect place or I've neglected to disconnect something important that causes the boiler to have constant power.

Any help or guidance on this would be really appreciated.
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by GEORGzer »

I can‘t tell from the photo but if there is currently nothing connected to „2“, move over the wire from „1“, so that there is nothing connected to „1“.

Then connect the Netatmo Relais as follows:
Brown to „2“
Blue to „3“
Black to „2“ as well
Grey to „1“
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
Moose
Posts: 3
Joined: 06 Jul 2020, 23:21

Re: Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by Moose »

GEORGzer wrote: 07 Jul 2020, 00:12 I can‘t tell from the photo but if there is currently nothing connected to „2“, move over the wire from „1“, so that there is nothing connected to „1“.

Then connect the Netatmo Relais as follows:
Brown to „2“
Blue to „3“
Black to „2“ as well
Grey to „1“
Thanks a million for this reply. Really appreciate it.

Looks like I tackled it completely wrong. I'll go rewire it now and let you know how I get on.

Cheers!
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by GEORGzer »

It‘s just a hunch because „Switched Live from Programmer“ means it‘s a live wire coming from a thermostat and if no thermostat is installed, they usually just connect the phase.

If nothing is connected to „2“ you can miss-use that terminal to connect the mentioned wires.
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee
Moose
Posts: 3
Joined: 06 Jul 2020, 23:21

Re: Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by Moose »

GEORGzer wrote: 07 Jul 2020, 20:14 It‘s just a hunch because „Switched Live from Programmer“ means it‘s a live wire coming from a thermostat and if no thermostat is installed, they usually just connect the phase.

If nothing is connected to „2“ you can miss-use that terminal to connect the mentioned wires.
Worked like a charm! Up and running for the last five hours without a hitch.

Thanks again for your help! You’ve built up plenty of good karma, cheers 👍🏻
GEORGzer
Posts: 2663
Joined: 14 Jan 2014, 18:14

Re: Grant 50/90 Oil Boiler: connecting the wireless Thermostat

Post by GEORGzer »

;)
Home: Weather Station (V3 + Rain & Wind Gauge, 3 additional Indoor Modules, Shield), Valves Starter Pack + 7 Valves, Video Doorbell
Office: Thermostat (V2), Healthy Home Coach, Smoke Alarm, 2 2in1 Sensors

Not a Netatmo employee